F01038 fault in siemens G120 Drive

1 Posts
1 Users
0 Reactions
228 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : ACX: Loading the parameter back-up file unsuccessful - comes when an error has occurred when downloading PSxxxyyy.ACX or PTxxxyyy.ACX files from the non-volatile memory.

If you have saved the project data using the commissioning software, download the project again. Save using the function "Copy RAM to ROM" or with p0971 = 1 so that all of the parameter files are again completely written to the non-volatile memory.

- replace the memory card or Control Unit.