F01340 fault in siemens G120 Drive

1 Posts
1 Users
0 Reactions
145 Views
Posts: 18069
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Topology - Too many components on one line comes when the selected communications clock cycle, too many DRIVE-CLiQ components are connected to one line of the Control Unit.

- check the DRIVE-CLiQ connection.
- Reduce the number of components on the DRIVE-CLiQ line involved and distribute these to other DRIVE-CLiQ sockets of the Control Unit. This means that communication is uniformly distributed over several lines.

Re fault value = 1yy - 4yy in addition:
- increase the sampling times (p0112, p0115, p4099). If necessary, for DCC or FBLOCKS, change the assignment of the run-time group (p21000, p20000) so that the sampling time (r21001, r20001) is increased.
- if necessary, reduce the number of cyclically calculated blocks (DCC) and/or function blocks (FBLOCKS).
- reduce the function modules (r0108).