Forum

Share:
Notifications
Clear all

F01600 fault in siemens G120 Drive

1 Posts
1 Users
0 Reactions
2,544 Views
Posts: 18069
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : SI P1: STOP A initiated - comes when the drive-integrated "Safety Integrated" function on processor 1 has detected an error and initiated a STOP A.

- forced checking procedure of the safety shutdown path on processor 1 unsuccessful.
- subsequent response to fault F01611 (defect in a monitoring channel).

Fault value (r0949, interpret decimal):
0: Stop request from processor 2.
1005: Pulses suppressed although STO not selected and there is no internal STOP A present.

- select Safe Torque Off and de-select again. For fault value = 9999:
- carry out diagnostics for fault F01611.

Note: STO: Safe Torque Off

Share: