F01650 fault in siemens G120 Drive

1 Posts
1 Users
0 Reactions
922 Views
Posts: 18069
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : SI P1: Acceptance test required comes when the drive-integrated "Safety Integrated" function on processor 1 requires an acceptance test.

Note: This fault results in a STOP A that can be acknowledged.

For fault value = 130:
- carry out safety commissioning routine. For fault value = 1000:
- again carry out safety commissioning routine.
- replace the memory card or Control Unit.
- Using STARTER, activate the safety parameters for the drive involved (change settings, copy parameters, activate settings).

For fault value = 2000:
- check the safety parameters on processor 1 and adapt the reference checksum (p9799).

For fault value = 2001:
- check the safety parameters on processor 2 and adapt the reference checksum (p9899).

For fault value = 2002:
- enable the safety-related functions on processor 1 and check processor 2 (p9601 = p9801).

Re fault value = 2003, 2004, 2005:
- Carry out an acceptance test and generate an acceptance report. The fault with fault value 2005 can only be acknowledged when the "STO" function is de-selected.

For fault value = 2020:
- again carry out safety commissioning routine.
- replace the memory card or Control Unit.

For fault value = 9999:
- carry out diagnostics for the other safety-related fault that is present.

Note: STO: Safe Torque Off
See also: p9799 (SI setpoint checksum SI parameters (processor 1)), p9899 (SI setpoint checksum SI parameters
(processor 2))