Cause : SI P1 PROFIsafe telegram number not suitable comes when the PROFIsafe telegram number in p60022 is unsuitable for the enabled safety functions.
Possible causes:
- When PROFIsafe is not enabled (p9601.3 = 0), then it is not permissible to select a PROFIsafe telegram in p60022.
- When PROFIsafe is enabled (p9601.3 = 1), then a PROFIsafe telegram must be selected in p60022.
- When the transfer of the F-DIs via PROFIsafe (p9501.30 = 1) is selected, then telegram 900 must be selected in p60022 (this only applies to Control Units, which support Extended Functions via PROFIsafe (r9771.4 = 1)).
Note: This fault does not result in a safety stop response.
See also: p9501, p9601, p60022