Cause : Supply voltage (p0210) incorrectly parameterized comes when the measured DC voltage lies outside the tolerance range after pre-charging has been completed. The following applies for the tolerance range: 1.16 * p0210 < r0070 < 1.6 * p0210.
- check the parameterized supply voltage and if required change (p0210).
- check the line supply voltage.