Cause : Motor overtemperature comes when the motor temperature has exceeded the fault threshold (p0605) or the timer (p0606) after the alarm threshold was exceeded (p0604) has expired. The response parameterized in p0610 becomes active. The alarm is withdrawn if the response threshold for wire breakage or sensor not connected is exceeded (R > 2120 Ohm).
PTC or bimetallic NC contact: The response threshold of 1650 Ohm was exceeded or the NC contact opened and the timer (p0606) has expired.
The response parameterized in p0610 becomes active. Possible causes:
- Motor is overloaded
- motor ambient temperature too high.
- Wire break or sensor not connected
- Reduce the motor load.
- check the ambient temperature and the motor ventilation.
- check the wiring and the connection of the PTC or bimetallic NC contact.
See also: p0604, p0605, p0606, p0612, p0625, p0626, p0627, p0628