Siemens SINAMICS G120 Drive
1
Posts
1
Users
0
Reactions
181
Views
Feb 15, 2024 7:35 am
Cause : Units changeove- Parameter limit violation due to units changeover comes when a changeover of units was initiated. This resulted in a violation of a parameter limit
Possible causes for the violation of a parameter limit:
- When rounding off a parameter corresponding to its decimal places, the steady-state minimum limit or maximum limit was violated.
- inaccuracies for the data type "FloatingPoint". In these cases, when the minimum limit is violated then the parameter value is rounded up and when the maximum limited is violated the parameter value is rounded down.
Check the adapted parameter values and if required correct.
See also: r9451 (Units changeover adapted parameters)