F07088 fault in siemens G120 Drive

1 Posts
1 Users
0 Reactions
181 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Units changeove- Parameter limit violation due to units changeover comes when a changeover of units was initiated. This resulted in a violation of a parameter limit

Possible causes for the violation of a parameter limit:
- When rounding off a parameter corresponding to its decimal places, the steady-state minimum limit or maximum limit was violated.
- inaccuracies for the data type "FloatingPoint". In these cases, when the minimum limit is violated then the parameter value is rounded up and when the maximum limited is violated the parameter value is rounded down.

Check the adapted parameter values and if required correct.
See also: r9451 (Units changeover adapted parameters)