F07320 fault in siemens G120 Drive

1 Posts
1 Users
0 Reactions
805 Views
Posts: 18018
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : Automatic restart interrupted comes when the specified number of restart attempts (p1211) has been completely used up because within the monitoring time (p1213) the faults were not able to be acknowledged. The number of restart attempts (p1211) is decremented at each new start attempt.

- there is no active ON command.
- the monitoring time for the power unit has expired (p0857).
- when exiting commissioning or at the end of the motor identification routine or the speed controller optimization, the drive unit is not automatically powered up again.

Remedy:

- increase the number of restart attempts (p1211). The actual number of starting attempts is displayed in r1214.
- increase the delay time in p1212 and/or the monitoring time in p1213.
- issue an ON command (p0840).
- either increase or disable the monitoring time of the power unit (p0857).
- Reduce the delay time for resetting the start counter (p1213[1]) so that fewer faults are registered in the time interval.