Forum

Share:
Notifications
Clear all

F07404 fault in siemens G120 Drive

1 Posts
1 Users
0 Reactions
1,240 Views
Posts: 18018
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : DC link voltage monitoring Vdc_Max comes when the monitoring of the DC link voltage p1284 has responded (only U/f control).

- check the line supply voltage.
- check the braking module.
- adapt the device supply voltage (p0210).
- adapt the DC link voltage monitoring (p1284).

Share: