Cause : DC link voltage monitoring Vdc_Max comes when the monitoring of the DC link voltage p1284 has responded (only U/f control).

- check the line supply voltage.
- check the braking module.
- adapt the device supply voltage (p0210).
- adapt the DC link voltage monitoring (p1284).