F07800 fault in siemens G120 Drive

3 Posts
2 Users
0 Reactions
5,505 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : No power unit present comes when the power unit parameters cannot be read or no parameters are stored in the power unit. It is possible that the DRIVE-CLiQ cable between the Control Unit and power unit is interrupted or defective.

- carry out a POWER ON (power off/on) for all components.
- check the DRIVE-CLiQ cable between the Control Unit and power unit.
- Check the power unit and replace if necessary.
- check the Control Unit, and if required replace it.
- after correcting the topology, the parameters must be again downloaded using the commissioning software

2 Replies
Posts: 1
(@amirmalekii77077)
New Member
Joined: 2 months ago

please help me to repair the  siemens g120 drive that indicate f7800 

Reply
1 Reply
Admin
(@click2electro)
Joined: 4 years ago

Member
Posts: 18330

@amirmalekii77077 check power card may be some issue in power supply section. Also check connecting cable of power card.

Reply