Forum

Share:
Notifications
Clear all

F07802 fault in siemens G120 Drive

1 Posts
1 Users
0 Reactions
2,159 Views
Posts: 18018
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

cause : Infeed or power unit not ready comes when after an internal power-on command, the infeed or drive does not signal ready.

- monitoring time is too short.
- DC link voltage is not present.
- associated infeed or drive of the signaling component is defective.
- supply voltage incorrectly set

Remedy:

- increase the monitoring time (p0857).
- ensure that there is a DC link voltage. Check the DC link busbar. Enable the infeed.
- replace the associated infeed or drive of the signaling component.
- check the line supply voltage setting (p0210).
See also: p0857 (Power unit monitoring time)

Share: