Siemens SINAMICS G120 Drive
1
Posts
1
Users
0
Reactions
483
Views
Feb 15, 2024 9:32 am
Cause : HF damping module- damping not ready comes when switching on or in the switched-on state, the HF damping module does not return a ready signal.
- Check the DRIVE-CLiQ wiring to the HF damping module.
- check the 24 V supply voltage.
- if required, replace the HF damping module