Siemens SINAMICS G120 Drive
1
Posts
1
Users
0
Reactions
579
Views
Feb 15, 2024 11:42 am
Cause : No cyclic connection comes when there is no connection to a PROFINET controller. Establish the cyclic connection and activate the controller with cyclic operation. Check the parameters "Name of Station" and "IP of Station" (r61000, r61001).