F08702 fault in siemens G120 Drive

1 Posts
1 Users
0 Reactions
136 Views
Posts: 18023
Admin
Topic starter
(@click2electro)
Member
Joined: 3 years ago

Cause : RPDO Timeout comes when the monitoring time of the CANopen RPDO telegram has expired because the bus connection was either interrupted or the CANopen Master was switched-off.

- check the bus cable
- check the master.
- If required, increase the monitoring time (p8699).