F30080 fault in siemens G120 Drive

1 Posts
1 Users
0 Reactions
188 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Current increasing too quickly comes when the power unit has detected an excessive rate of rise in the overvoltage range.

- closed-loop control is incorrectly parameterized.
- motor has a short-circuit or fault to ground (frame).
- U/f operation: Up ramp set too low.
- U/f operation: rated current of motor much greater than that of power unit.
- power cables are not correctly connected.
- power cables exceed the maximum permissible length.
- power unit defective.

Fault value (r0949, interpret bitwise binary):
Bit 0: Phase U.
Bit 1: Phase V.
Bit 2: Phase W.

  1. check the motor data - if required, carry out commissioning.
  2. check the motor circuit configuration (star-delta)
  3. U/f operation: Increase up ramp.
  4. U/f operation: Check assignment of rated currents of motor and power unit.
  5. check the power cable connections.
  6. check the power cables for short-circuit or ground fault.
  7. check the length of the power cables.
  8. replace power unit.