F30655 fault in siemens G120 Drive

1 Posts
1 Users
0 Reactions
346 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Align monitoring functions comes when an error has occurred when aligning the Safety Integrated monitoring functions on processor 1 and processor 2. No common set of supported SI monitoring functions was able to be determined.

- there is a communication error between processor 1 and processor 2 or communication has failed.

- carry out a POWER ON (power off/on).

- check the electrical cabinet design and cable routing for EMC compliance