F30682 fault in siemens G120 Drive

1 Posts
1 Users
0 Reactions
269 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Monitoring function not supported comes when the monitoring function enabled in p9301, p9501, p9601 or p9801 is not supported in this firmware version.

Fault value (r0949, interpret decimal):

1: Monitoring function SLP not supported (p9301.1).
2: Monitoring function SCA not supported (p9301.7 and p9301.8 ... 15).
3: Monitoring function SLS override not supported (p9301.5).
4: Monitoring function external ESR activation not supported (p9301.4).
5: Monitoring function F-DI in PROFIsafe not supported (p9301.30).
6: Enable actual value synchronization not supported (p9301.3).
9: Monitoring function not supported by the firmware or enable bit not used.
24: Monitoring function SDI not supported.

Deselect the monitoring function involved.