Forum

Share:
Notifications
Clear all

F30809 fault in siemens G120 Drive

1 Posts
1 Users
0 Reactions
188 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

cause : Switching information not valid comes when the last switching status word in the setpoint telegram is identified by the end ID. Such an end ID was not found.

- carry out a POWER ON (power off/on) for all components.
- upgrade firmware to later version.

Share: