F31912 fault in siemens G120 Drive

1 Posts
1 Users
0 Reactions
264 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

cause : Device combination is not permissible comes when the selected device combination is not supported or in compatible device.

Fault value (r0949, interpret decimal):
1003: The connected measuring unit cannot be operated with the EnDat 2.2 converter. For instance, the measuring unit has a pulse number/resolution of 2^n.

1005: The type of measuring unit (incremental) is not supported by the EnDat 2.2 converter.

1006: The maximum duration (31.25 μs) of the EnDat transfer was exceeded.

2001: The set combination of current controller cycle, DP cycle and Safety cycle is not supported by the EnDat 2.2 converter.

2002: The resolution of the linear measuring unit does not match the pole pair width of the linear motor

Re fault value = 1003, 1005, 1006: Use a measuring unit that is permissible.

For fault value = 2001: Set a permissible cycle combination (if required, use standard settings).

For fault value = 2002: Use a measuring unit with a lower resolution (p0422).