F32912 fault in siemens G120 Drive
cause : Device combination is not permissible comes when the selected device combination is not supported.
1003: The connected measuring unit cannot be operated with the EnDat 2.2 converter. For instance, the measuring unit has a pulse number/resolution of 2^n.
1005: The type of measuring unit (incremental) is not supported by the EnDat 2.2 converter.
1006: The maximum duration (31.25 μs) of the EnDat transfer was exceeded.
2001: The set combination of current controller cycle, DP cycle and Safety cycle is not supported by the EnDat 2.2 converter.
2002: The resolution of the linear measuring unit does not match the pole pair width of the linear motor.
Re fault value = 1003, 1005, 1006: Use a measuring unit that is permissible.
For fault value = 2001: Set a permissible cycle combination (if required, use standard settings).
For fault value = 2002: Use a measuring unit with a lower resolution (p0422).