F50518 fault in siemens G120 Drive

1 Posts
1 Users
0 Reactions
418 Views
Posts: 18313
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

cause : Sampling time of free run-time group differs at download comes when the STARTER/SCOUT project that was downloaded, the hardware sampling time of a free run-time group (1 <= p20000[i] <= 256) was set to a value that was either too low or too high.

  1. The sampling time must be between 1 ms and the value r20003 - r20002.
  2. If the sampling time of the selected free run-time group is < 1 ms, the equivalent value of 1 ms is used.
  3. If the value >= r20003, then the sampling time is set to the next higher or the same software sampling time >= r21003.

- correctly set the sampling time of the run-time group.
- if required, take all of the blocks from the run-time group.