Siemens SINAMICS G120 Drive
1
Posts
1
Users
0
Reactions
190
Views
Feb 16, 2024 3:17 pm
Cause : Technology controller parameterizing error comes when the technology controller has a parameterizing error.
Alarm value (r2124, interpret decimal): 1: The upper output limit in p2291 is set lower than the lower output limit in p2292.
Re alarm value = 1:
Set the output limit in p2291 higher than in p2292.
See also: p2291 (Technology controller maximum limiting), p2292 (Technology controller minimum limiting)