N07435 in siemens G120 Drive
1 Users
0 Reactions
Admin
Topic starter
(@click2electro)
Member
Cause : Setting the ramp-function generator for sensorless vector control comes when operation with sensorless vector control (r1407.1) the ramp-function generator was stopped (p1141). An internal setting command of the ramp-function generator output caused the set setpoint speed to be frozen.
- de-activate the holding command for the ramp-function generator (p1141).
- suppress the fault (p2101, p2119). This is necessary if the ramp-function generator is held using jogging and the speed setpoint is simultaneously inhibited (r0898.6).
Share: