Siemens SINAMICS G120 Drive
1
Posts
1
Users
0
Reactions
215
Views
Feb 16, 2024 4:38 pm
Cause : motor data identification not performed comes when the "vector control" mode has been selected and a motor data identification has still not been performed.
The alarm is initiated when changing the drive data set (see r0051) in the following cases:
- vector control is parameterized in the actual drive data set (p1300 >= 20). and
- motor data identification has still not been performed in the actual drive data set (see r3925).
- Perform motor data identification (see p1900).
- If required, parameterize "U/f control" (p1300 < 20).
- switch over to a drive data set, in which the conditions do not apply