N31460 in siemens G120 Drive

1 Posts
1 Users
0 Reactions
157 Views
Posts: 18454
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Analog sensor channel A failed comes when the input voltage of the analog sensor is outside the permissible limits.

Alarm value (r2124, interpret decimal):

1: Input voltage outside detectable measuring range.
2: Input voltage outside measuring range set in p4673.
3: The absolute value of the input voltage has exceeded the range limit (p4676)

Re alarm value = 1: check the output voltage of the analog sensor.
Re alarm value = 2: check the voltage setting for each encoder period (p4673).
Re alarm value = 3: check the range limit setting and increase it if necessary (p4676)