Cause : Analog sensor position value exceeds limit value comes when the position value has exceeded the permissible range of -0.5 ... +0.5.

Alarm value (r2124, interpret decimal):

1: Position value from the LVDT sensor.
2: Position value from the encoder characteristic.

Re alarm value = 1:
- Check the LVDT ratio (p4678).
- check the reference signal connection at track B.

Re alarm value = 2:
- check the coefficients of the characteristic (p4663 ... p4666).