Cause : Error in the component trace comes when an error has occurred in the component trace due to upload trace data (p7792 = 1), change factory setting (p7790, p7791) for missing property "component trace" (r0193.1 = 0).
The message appears in the following cases:
- upload trace data (p7792 = 1).
- change factory setting (p7790, p7791) for missing property "component trace" (r0193.1 = 0).
Alarm value (r2124, interpret decimal):
1: The DRIVE-CLiQ component does not support the component trace (r0193.1 = 0).
101: Data from trace 1 cannot be read.
102: Data from trace 2 cannot be read.
103: Data from trace 3 cannot be read.
104: Data from trace 4 cannot be read.
105: Data from trace 5 cannot be read.
Re alarm value = 1: Upgrade the firmware of the DRIVE-CLiQ component involved.