A01324 alarm in siemens S120 Drive

1 Posts
1 Users
0 Reactions
252 Views
Posts: 19965
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Dummy drive object number incorrectly created comes when in p0978, dummy drive object numbers (255) are only permitted in the first partial list.

Set p0009 to 1 and change p0978: Rules
- p0978 must include all of the drive object numbers (p0101).
- it is not permissible for a drive object number to be repeated.
- by entering a 0, the drive objects with PZD are separated from those without PZD.
- only 2 partial lists are permitted. After the second 0, all values must be 0.
- dummy drive object numbers (255) are only permitted in the first partial list.