A01331 alarm in siemens S120 Drive

1 Posts
1 Users
0 Reactions
610 Views
Posts: 19965
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : At least one component not assigned to a drive object comes when at least one component is not assigned to a drive object.

  1. when commissioning, a component was not able to be automatically assigned to a drive object.
  2. the parameters for the data sets are not correctly set.

This component is assigned to a drive object. Check the parameters for the data sets.

Examples:

- power unit (p0121).
- motor (p0131, p0186).
- encoder interface (p0140, p0141, p0187 ... p0189).
- encoder (p0140, p0142, p0187 ... p0189).
- Terminal Module (p0151).
- option board (p0161).