Cause : power unit incorrectly inserted comes when topology comparison has detected a power unit in the actual topology that has been incorrectly inserted.
Adapting topologies:
- insert the components involved at the right connection (correct the actual topology).
- adapt the project/parameterization in the commissioning software (correct the target topology).
- automatically remove the topology error (p9904).