A01389 alarm in siemens S120 Drive

1 Posts
1 Users
0 Reactions
307 Views
Posts: 19847
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Motor with DRIVE-CLiQ incorrectly inserted comes when the topology comparison has detected a motor with DRIVE-CLiQ in the actual topology that has been incorrectly inserted with respect to the target topology.

Alarm value (r2124, interpret hexadecimal):

ddccbbaa hex:
dd = connection number (%4)
cc = component number (%3)
bb = component class (% 2)
aa = component number of the incorrectly inserted component (% 1)

Adapting topologies:

- insert the components involved at the right connection (correct the actual topology).
- adapt the project/parameterization in the commissioning software (correct the target topology).
- automatically remove the topology error (p9904).