Siemens SINAMICS S120/S150 Drive
1
Posts
1
Users
0
Reactions
599
Views
Feb 19, 2024 12:17 pm
Cause : Incorrect connection used comes whenthe topology comparison has detected differences in the actual and target topologies in relation to one component.
Adapting topologies:
- reinsert the DRIVE-CLiQ cable to the component (correct the actual topology).
- adapt the project/parameterization in the commissioning software (correct the target topology).
- automatically remove the topology error (p9904).