A01484 alarm in siemens S120 Drive

1 Posts
1 Users
0 Reactions
211 Views
Posts: 19860
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : DRIVE-CLiQ Hub Module not inserted comes whenthe topology comparison has detected a DRIVE-CLiQ Hub Module missing in the actual topology with respect to the target topology.

Adapting topologies:

- insert the components involved at the right connection (correct the actual topology).
- adapt the project/parameterization in the commissioning software (correct the target topology).

Check the hardware:

- check the 24 V supply voltage.
- check DRIVE-CLiQ cables for interruption and contact problems.
- check that the component is working properly.