Siemens SINAMICS S120/S150 Drive
1
Posts
1
Users
0
Reactions
378
Views
Feb 19, 2024 12:33 pm
Cause : Interconnections to inactive objects present comes when there are BICO interconnections to an inactive/inoperable drive object.
- The BI/CI parameters involved are listed in r9498.
- The associated BO/CO parameters are listed in r9499.
- The list of the BICO interconnections to other drive objects is displayed in r9491 and r9492 of the de-activated drive object.
- set all open BICO interconnections centrally to the factory setting with p9495 = 2.
- make the non-operational drive object active/operational again (re-insert or activate components).