A01784 alarm in siemens S120 Drive
Cause : SBT brake test canceled with fault comes when the safe brake test was canceled as a result of a fault.
Alarm value (r2124, interpret binary):
Bit 17 = 1: fault in the brake test sequence (cause, see bits 0 ... 10).
Bit 18 = 1: the internal brake is closed. It must be open when the external brake is tested (p10202).
Bit 19 = 1: the external brake is closed. It must be open when the internal brake is tested (p10202).
Bit 20 = 1: not all brakes are open (p10202).
Bit 21 = 1: axis position during the brake test not valid due to parking axis.
Bit 22 = 1: internal software error.
Bit 23 = 1: the permissible position range of the axis was violated with the brake closed (p10212/ p10222).
Bit 24 = 1: the tested internal brake was opened while the brake test was active.
Bit 25 = 1: the tested external brake was opened while the brake test was active.
Bit 26 = 1: during the active brake test, the test torque left its tolerance bandwidth (20 %).
Cause for alarm value bit 17:
Bit 0 = 1: operation when selecting the brake test not enabled (r0899.2 = 0).
Bit 1 = 1: external fault occurred (e.g. the brake test that has already started is canceled by the user).
Bit 2 = 1: when selecting the brake test a brake is closed.
Bit 3 = 1: when determining the load torque a brake is closed.Bit 4 = 1: a fault with a stop response has occurred (e.g.. OFF1, OFF2 or OFF3).
Bit 5 = 1: when selecting the brake test the axis speed setpoint is too high.
Bit 6 = 1: the actual speed (r0063) of the axis is too high (e.g. brake does not hold during the brake test).
Bit 7 = 1: incorrect speed controller mode (e.g. encoderless speed control or U/f operation).
Bit 8 = 1: closed-loop control not enabled or function generator active.
Bit 9 = 1: control does not switch over to the brake test (e.g. because PI speed control has not been parameterized).
Bit 10 = 1: torque limit reached (r1407.7, r1408.8).
- Remove the fault cause.
- Carry out a safe acknowledgment.
- If required, restart the brake test.
Re bit 17 = 1 with bit 6 = 1 or bit 23 = 1: If the brake closing time of the motor holding brake (p1217) has been set too low, then at the start of the brake test, the brake is closed too late. The brake closing time should be adapted (p1217).