A01788 alarm in siemens S120 Drive

1 Posts
1 Users
0 Reactions
331 Views
Posts: 18455
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : wait for STO deselection via SMM comes when the STO function is selected via Safety Extended Functions or a safety message is present, which results in STO. The automatic test stop was not able to be carried out since the power up. The automatic test stop is performed after deselecting STO.

  1. Deselect STO via Safety Extended Functions.
  2. Remove the cause of the safety message and acknowledge the fault.