A01789 alarm in siemens S120 Drive

1 Posts
1 Users
0 Reactions
234 Views
Posts: 18455
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Automatic test stop and brake test not permitted when test stop is selected comes when the parameterization of the automatic test stop (p9507.6/p9307.6) and the brake test when a test stop is selected (p10203 = 2) is not permissible. The test stop is not automatically carried out when the powering up.

- correct the parameter assignment.
- set p10203 not equal to 2 or deactivate the automatic test stop.