A01982 alarm in siemens S120 Drive

1 Posts
1 Users
0 Reactions
253 Views
Posts: 18163
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Second controller missing comes when the PROFINET function "Shared Device" has been activated (p8929 = 2). However, only the connection to a PROFINET controller is present.

  • Check the configuration of the PROFINET controllers as well as the p8929 setting.