A02095 alarm in siemens S120 Drive

1 Posts
1 Users
0 Reactions
156 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Multiple trace cannot be activated comes when the following functions or settings are not permissible in conjunction with a multiple trace (trace recorder 0):

- measuring function
- long-time trace
- trigger condition "immediate recording start" (IMMEDIATE)
- trigger condition "start with function generator" (FG_START)

Remedy:

  • if required, deactivate the multiple trace (p4840[0] = 0).
  • deactivate function or setting that is not permissible.
  • See also: p4840 (MTrace cycle number setting).