Siemens SINAMICS S120/S150 Drive
1
Posts
1
Users
0
Reactions
132
Views
Feb 21, 2024 6:53 am
Cause : Multiple trace cannot be activated comes when the following functions or settings are not permissible in conjunction with a multiple trace (trace recorder 1):
- measuring function
- long-time trace
- trigger condition "immediate recording start" (IMMEDIATE)
- trigger condition "start with function generator" (FG_START)
- if required, deactivate the multiple trace (p4840[1] = 0).
- deactivate function or setting that is not permissible
- See also: p4840 (MTrace cycle number setting)