A02098 alarm in siemens S120 Drive

1 Posts
1 Users
0 Reactions
221 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Cannot be saved comes when it is not possible to save the measurement results of a multiple trace on the memory card (trace recorder 1). A multiple trace is not started or is canceled.

Alarm value (r2124, interpret decimal):

1: Memory card cannot be accessed.
- card is not inserted or is blocked by a mounted USB drive.

3: data save operation to slow.
- a second trace has been completed before the measurement results of the first trace were able to be saved.
- writing the measurement result files to the card is blocked by the parameter save.

4: Data save operation canceled.
- for instance, the file required for the data save operation was not able to be found.
See also: p4840 (MTrace cycle number setting)

- insert or remove the memory card.
- use a larger memory card.
- configure a longer trace time or use an endless trace.
- avoid saving parameters while a multiple trace is running.
- check whether other functions are presently accessing measurement result files.