Siemens SINAMICS S120/S150 Drive
1
Posts
1
Users
0
Reactions
137
Views
Feb 21, 2024 6:58 am
Cause : Insufficient Control Unit memory comes when the memory space still available on the Control Unit is no longer sufficient for the trace function.
Reduce the memory required, e.g. as follows:
- reduce the trace time.
- increase the trace clock cycle.
- reduce the number of signals to be traced.
See also: r4708 (Trace memory space required), r4799 (Trace memory location free).