A02100 alarm in siemens S120 Drive

1 Posts
1 Users
0 Reactions
335 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Computing dead time current controller too short comes when the value in p0118 produces a dead time of one clock cycle because it is prior to set point availability.

Possible causes:
- A parameter backup with a version higher than 4.3 was loaded to a version less than or equal to 4.3.
- The system properties after replacing a component no longer match the parameter assignment.

- set p0118 to zero.
- set p0118 to a value greater than or equal to the alarm value (for p1810.11 = 1)
- set p0117 (from the device) to an automatic setting (p0117 = 1).
- check the firmware versions of the components involved.
See also: p0117 (Current controller computing dead time mode), p0118 (Current controller computing dead time)