A06207 alarm in siemens S120 Drive

1 Posts
1 Users
0 Reactions
245 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Line currents not symmetrical comes when asymmetry of the currents in the line phase too high. The most probable cause is failure of a line phase.

- check the line supply and fuses.
- check the connection and size (rating) of the line reactor.
- check the previous alarm A06205 and the alarm value.