F01012 fault in siemens S120 Drive

1 Posts
1 Users
0 Reactions
175 Views
Posts: 18330
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Project conversion error comes when converting the project of an older firmware version, an error occurred.

Fault value (r0949, interpret decimal):

Parameter number of the parameter causing the error.

For fault value = 600, the following applies:

  1. The temperature evaluation is no longer assigned to the power unit but to the encoder evaluation.
  2. Check the parameter indicated in the fault value and correctly adjust it accordingly.

For fault value = 600:

Parameter p0600 must be set to the values 1, 2 or 3 in accordance with the assignment of the internal encoder evaluation to the encoder interface.

  • Value 1 means: The internal encoder evaluation is assigned to the encoder interface 1 via p0187.
  • Value 2 means: The internal encoder evaluation is assigned to the encoder interface 2 via p0188.
  • Value 3 means: The internal encoder evaluation is assigned to the encoder interface 3 via p0189.

- If necessary, the internal encoder evaluation must be assigned to an encoder interface via parameters p0187, p0188 or p0189 accordingly.

- If necessary, upgrade the firmware to a later version.