F01303 fault in siemens S120 Drive
Cause : Component does not support the required function comes when a function requested by the Control Unit is not supported by a DRIVE-CLiQ component.
1: The component does not support the de-activation.
101: The Motor Module does not support an internal armature short-circuit.
102: The Motor Module does not support the de-activation.
201: The Sensor Module does not support actual value inversion (p0410.0 = 1) when using a Hall sensor (p0404.6 = 1) for the commutation.
202: The Sensor Module does not support parking/unparking.
203: The Sensor Module does not support the de-activation.204: The firmware of this Terminal Module 15 (TM15) does not support the application TM15DI/DO.
205: The Sensor Module does not support the selected temperature evaluation (r0458).
206: The firmware of this Terminal Modules TM41/TM31/TM15 refers to an old firmware version. It is urgently necessary to upgrade the firmware to ensure disturbance-free operation.
207: The power unit with this hardware version does not support operation with device supply voltages of less than 380 V.
208: The Sensor Module does not support de-selection of commutation with zero mark (via p0430.23).
211: The Sensor Module does not support single-track encoders (r0459.10).
212: The Sensor Module does not support LVDT sensors (p4677.0).
213: The Sensor Module does not support the characteristic type (p4662)
Upgrade the firmware of the DRIVE-CLiQ component involved.
For fault value = 205: Check parameter p0600 and p0601 and if required, adapt interpretation.
For fault value = 207: Replace the power unit or if required set the device supply voltage higher (p0210).
For fault value = 208: Check parameter p0430.23 and reset if necessary.