Cause : Too many components on one line comes when the selected communications clock cycle, too many DRIVE-CLiQ components are connected to one line of the Control Unit.
- check the DRIVE-CLiQ wiring.
- Reduce the number of components on the DRIVE-CLiQ line involved and distribute these to other DRIVE-CLiQ sockets of the Control Unit. This means that communication is uniformly distributed over several lines.