F01612 fault in siemens S120 Drive

1 Posts
1 Users
0 Reactions
325 Views
Posts: 18456
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : STO inputs for power units connected in parallel different comes when the drive-integrated "Safety Integrated" function on the Control Unit (CU) has identified different states of the AND'ed STO inputs for power units connected in parallel and has initiated a STOP F.

As a result of this fault, after the parameterized transition has expired (p9658), fault F01600 (SI CU: STOP A initiated) is output.

- check the tolerance time SGE changeover and if required, increase the value (p9650).
- check the wiring of the safety-relevant inputs (SGE) (contact problems).