Siemens SINAMICS S120/S150 Drive
1
Posts
1
Users
0
Reactions
325
Views
Feb 19, 2024 12:54 pm
Cause : STO inputs for power units connected in parallel different comes when the drive-integrated "Safety Integrated" function on the Control Unit (CU) has identified different states of the AND'ed STO inputs for power units connected in parallel and has initiated a STOP F.
As a result of this fault, after the parameterized transition has expired (p9658), fault F01600 (SI CU: STOP A initiated) is output.
- check the tolerance time SGE changeover and if required, increase the value (p9650).
- check the wiring of the safety-relevant inputs (SGE) (contact problems).