F01674 fault in siemens S120 Drive

1 Posts
1 Users
0 Reactions
182 Views
Posts: 18455
Admin
Topic starter
(@click2electro)
Member
Joined: 4 years ago

Cause : Safety function not supported by PROFIsafe telegram comes when the monitoring function enabled in p9501 and p9601 is not supported by the currently set PROFIsafe telegram (p9611).

- Deselect the monitoring function involved (p9501, p9601).
- set the matching PROFIsafe telegram (p9611).